Relative Reduction in Embedded Depth

Posted by IAN WILLIAMSabout 4 years ago
Relative Reduction in Embedded Depth

For an M24 HAS-U 5.8 with HVU2 Capsule the recommended embedded depth is 210mm in 270mm concrete, if I cannot achieve this, and use 150mm embedment in 200mm concrete is the reduction in design resistance linear?
Therefore, design resistance is 99.8kN @ 210mm depth, so @ 150mm depth this would be 71.25kN – a 28.6% reduction in effective embedment and pull out resistance?

Embedded Depth,HVU2

1 Reply
Posted by Lillian Wongabout 4 years ago

Dear Williams

Thank you for contacting Hilti.

We are not recommended to assuming the loading by this method, our loading data is from European ETA test report, if you are using a embedment depth which is out of testing Range.Since the ETA is not covered, there will be not any test report Data to support your calculations.
if you need any further design support please feel free to contact us by email : TeamEngineering.HK@hilti.com


Any technical advice, calculations or recommendations contained in this email must be reviewed and cleared by your expert (including appropriately qualified engineers) prior to using them for your specific facility or incorporating into your final decision / design. They are based on information that we are provided and Hilti does not guarantee the absence of errors, the completeness and suitability for specific applications.

Best regards,